F fifty five Member Apr 26, 2009 #1 installing emt conduit outside compression fittings non hazardous is it acceptable
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 26, 2009 #2 Make sure your fittings are listed as raintight, see 225.22 Roger