Can you put romex in pvc?are there any exceptions??
I also concur but in NJ some state official don't agree for conduit systems.
Is there a local amendment or is this that they just don't like it?
Chris
Other than the dry location requirement, two items you might want to consider. If you are actually installing NM in conduit, check Note 9, Chapter 9 (pg 671-'08 Code) about sizing the conduit to the cable, and if you are "sleeving" romex coming into a panel note the restrictions in 312.5(C).Can you put romex in pvc?are there any exceptions??