Electrified Furniture

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Just curious. Furniture in-feeds each 3ckt/6 wire. They show them a direct homeruns for each 3ckt furniture. Would you figure it that way? Why couldn't you combine each of the 3ckt in the ceiling and run one 6ckt homerun back? Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    22.5 KB · Views: 9
That’s just showing what you need at each location; how you get it there is up to you. But you’re going to have 6 CCC’s at each box, so if you combine them to one conduit, de-rating factors will apply.

Each furniture piece is going to have a whip with 3 circuits coming out of it. You just need to put a box at each location with 3 circuits each.

The last several I’ve done had a carflex whip with one dedicated circuit and one multiwire circuit. Pull a neutral for each to be safe but you may have to go back and install handle ties if yours have multiwire circuits.


Sent from my iPhone using Tapatalk
 
That’s just showing what you need at each location; how you get it there is up to you. But you’re going to have 6 CCC’s at each box, so if you combine them to one conduit, de-rating factors will apply.

Each furniture piece is going to have a whip with 3 circuits coming out of it. You just need to put a box at each location with 3 circuits each.

The last several I’ve done had a carflex whip with one dedicated circuit and one multiwire circuit. Pull a neutral for each to be safe but you may have to go back and install handle ties if yours have multiwire circuits.


Sent from my iPhone using Tapatalk

Yes, thanks. Stub-up for tele/data and whip from wall box to furniture for both power and tele/data.
 
That’s just showing what you need at each location; how you get it there is up to you. But you’re going to have 6 CCC’s at each box, so if you combine them to one conduit, de-rating factors will apply.

^^this
 