beanland
Senior Member
- Location
- Vancouver, WA
I just had an opportunity to review the new proposed 626 on electrified truck parking. I have been involved in the design of several such facilities as well as RV parks. I am dismayed to see NFPA mandating that 3, and only 3, receptacles must be provided and that one of them must be a 30A 4-wire pin & sleeve connection. No truck manufacturer now equips trucks with pin & sleeve connections for shore power. In addition, only two legs of a 208Y/120V can be used with the pin & sleeve. For a brand new section of the NEC with no such facilities even being used, this section appears to be specifying the design rather than requiring safe construction. I would recommend that the specifics of the connections be allowed to evolve, rather than be codified. The requirements for conductors, load levels, disconnects and GFCI are all appropriate for safety.