I am investigating an electrocution that occurred in a baptismal. The baptismal had a 120V water pump and 208V water heaters. Testing revealed that the source of the electrical contact with the water was the electric heaters. The victim was immersed up to the chest area and made contact with ground by grabbing a microphone. Another person was also in the water and was shocked when they grabbed for the microphone, but not seriously injured.
The heaters were assembled by a local electrician and mounted to the tub wall. The metal casing of the heaters was not bonded.
The local electrical inspector stated that there should have been a GFCI breaker installed. I found that there is no requirement for GFCI on electric water heaters in NEC 680, 422 or 427. Should there be? Is this important enough to be required in the NEC??
The heaters were assembled by a local electrician and mounted to the tub wall. The metal casing of the heaters was not bonded.
The local electrical inspector stated that there should have been a GFCI breaker installed. I found that there is no requirement for GFCI on electric water heaters in NEC 680, 422 or 427. Should there be? Is this important enough to be required in the NEC??