Electrode Required or Prohibited ?
amptech
Indiana
Here is the situation:
Existing small church with a 200A 1? service. A gym/fellowship hall is being built and will connect to the existing church via 15' enclosed breezeway. The building code requires there to be fire separation between the church and the new addition and declares the addition a separate structure. 2 layers of 5/8" sheet rock are installed on the outside of the wall, under the vinyl siding facing the existing church. Automatic closing fire doors are installed at the new addition end of the connecting breezeway.
The electrical design calls for the original 200A service to be upgraded to a 320A meter-main with 200A feeding the existing panel in the church and 200A feeding a panel in the new addition via a 2-1/2" PVC conduit underground from the meter location to the panel location in the new addition. This route was used to avoid feeding the new building with a feeder passing through the existing building.(230.3). The feeder to the new addition will be 4 wire and a CEE was installed at the panel location in the new addition. EGC and the grounded conductor of the feeder will not be bonded at the new panel and the CEE conductor will terminate in the EGC bar in the new panel.
Here's the problem: The local inspector is forbidding the connection of the CEE to the new panel. He maintains that the breezeway connection makes both buildings one structure. He agrees that a 4 wire feeder is required and the EGC and grounded conductor should not be bonded in the new panel but insists the connection of the CEE or any other grounding electrode to the new panel is a code violation. I maintain that since the building code plan review has determined that the addition is a separate structure, the requirements of 250.32(A) must be satisfied. All NEC references in this post are 2008NEC. Opinions(with NEC reference) wanted.