We have 1,200A (100% rated electronic breaker) in a switchboard, according to NEC, we have to run (3) sets of 4#600kCM out of this breaker.
Contractor proposes to run (3) sets of 4#500kCM out of this breaker, in order to do this, he will adjusts the setting at the breaker lower than 100% (I guess around 1,100A).
(3) sets of 500KCM will be good for 1,140A so it should be okay with 1,100A load setting, I guess.
Will this be acceptable with NEC?