There is a situation where a 480V 200 HP motor and Allen-Bradley drive are pumping chilled water. The system was designed for additions to a loop that has not expanded to its full potential. The drive runs constantly at 30- 35 Hz at what flow I am not sure but could find out if that is needed.
There has been a lot of nusance tripping of the 600A Micrologic circuit breaker. The circuit breaker has been checked and tested, both by primary injection and secondary injection methods and is fine. I suspect that the motor and drive are severly oversized for the actual load but lack the mechanical expertise to say for sure.
Is there a reason that a large motor and drive running at less than a third FLA would trip an electronic circuit breaker? The drive guys want a thermal magnetic breaker but I am afraid of the lack of ground fault protection. The next ground fault protection is the 3000A main circuit for the switchboard.
There has been a lot of nusance tripping of the 600A Micrologic circuit breaker. The circuit breaker has been checked and tested, both by primary injection and secondary injection methods and is fine. I suspect that the motor and drive are severly oversized for the actual load but lack the mechanical expertise to say for sure.
Is there a reason that a large motor and drive running at less than a third FLA would trip an electronic circuit breaker? The drive guys want a thermal magnetic breaker but I am afraid of the lack of ground fault protection. The next ground fault protection is the 3000A main circuit for the switchboard.