151207-2001 EST
Ripter:
The questions I ask you were intended to stimulate thought. I don't plan to answer them, but to make some observations.
What I say below is not intended to imply what I would or wouldn't do, or suggest to be done.
The intent of your original post seemed to be directed to:
I'm concerned that much of our modern electronics probably need a ground to operate as designed.
What is ground? Is it just an EGC? Do most laptop computers, cellphone chargers, TVs, hairdryers, electric drills with double insulation, and many other devices with internal electronics have a two or three prong AC power cord plug.
An EGC is a normally non-current carrying conductor connected (bonded) to the neutral only at the main panel, and in turn is grounded (earthed) by an approved means. The purpose of an EGC is to provide a means to connect all exposed conductive surfaces on any electrical equipment connected to the EGC to earth.
Under normal conditions this should mean that the electrical potential between any electrical devices connected to the EGC and other conductive objects (cement floors, plumbing pipes, gas pipes, etc) is near zero volts and a human touching both should not get a shock.
It also means that leakage current within an EGC connected device should not appreciably raise the potential of the EGC at the leakage point relative to earthed conductive objects. If the EGC connected equipment is connected to a GFCI protected circuit, then this also means that the leakage current can not exceed the threshold limit of the GFCI for very long without tripping the GFCI.
If the circuit is not GFCI protected (a GFCI takes time to respond so it provides no protection for a short time), then a dead short between the hot conductor in the electrical equipment to the EGC in that equipment can raise the EGC potential at the shorting point relative to earth to approximately 1/2 the voltage of the hot conductor (multiply the RMS value by 1.414 to get the peak voltage) until the circuit breaker for the circuit opens. In some cases this will destroy electronic equipment. In particular un-isolated RS232, 422, 485, and USB circuits. Ethernet endpoints are usually isolated by a transformer.
Different pieces of electronic equipment connected together via non-isolated paths should have all the AC cords originate from the same receptacle. Not complete protection, but good protection from shorts outside of the said equipment.