Re: electrostatic transformers
IMO -A 480V delta to 480/277 wye transformer can provide some advantages:
1. Reduces fault current, especially if the upstream 480V system is fed by a large transformer (2500 kVA). The lower fault current may allow panels and breakers with lower short circuit ratings (=cheaper). Arc flash hazard may be reduced also.
2. Makes coordination of ground fault protection easier. A ground fault on the 480/277V side will only be seen as a phase-phase load on the upstream 480V system. This allows the upstream GF tripping devices to be set to trip faster.
These advantages have to be weighed against the disadvantages: additional kW losses, additional voltage drop on motor starting, plus the added transformer, secondary protection and panel and the space they take.