Just got plan checked on 620-22(b), dedicated branch circuit for elevator car air conditioning, even though there is no air conditioning, or requirement. The 99 code was adapted here, are you just providing a 15A, 120v circuit to meet this?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Elevator Air Cond. Circuit

Nvcape, I have wired alot of elevators in (4) states and have never seen a design calling for a circuit that wasn't needed.

The elevators I have wired with heat were served with the required source, even had one with a 208 1ph unit heater, they were all 20 amp circuits.

Roger
 

nvcape

Senior Member
Re: Elevator Air Cond. Circuit

Roger, thanks for the reply. The 99 code is not that old here, so can use some help. NFPA 3-9.4 requires that a heat detector shuts off elevator power before sprinkler operation. Elsewhere(3-9.3), it tells you to use a smoke also in the shaft and equipment room to lower the car first; but no where that I know of does it tell you to have controls to make sure the car is lowered before you kill power. We also are required to add an auxillary contact to kill the battery power too. How do other areas handle this. Next, are they requiring you to kill the cab lights and air conditioning too?
 

ron

Senior Member
Re: Elevator Air Cond. Circuit

There is no national requirement to ensure that the car is at a floor prior to elevator power shunt trip.
Consider that the smoke detector at the top of the shaft will begin recall well in advance of the temperature reaching 135 (heat detector) or 165 degrees (sprinkler head).
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: Elevator Air Cond. Circuit

My read on this is as follows: IF an A/C unit is installed, THEN it must be served by a dedicated branch circuit. I may be splitting a very fine hair here, but I believe the key to understanding 620-22(B) (1999 version) is to focus on the first sentence, and in particular upon the single occurrence of the word ?the.? The exact wording of this sentence is, ?A dedicated branch circuit shall supply THE (my emphasis) air-conditioning and heating units on each elevator car.? This does not require that an A/C unit be installed, nor that a dedicated branch circuit be provided, just in case the owner decides to install an A/C unit sometime in the future. If there is no A/C unit, then you don?t need to install a dedicated branch circuit for an A/C unit.

Good luck on this one. The Inspector might read the article differently, and can easily call it the other way.
 

nvcape

Senior Member
Re: Elevator Air Cond. Circuit

Learned a little more. The NFPA 2002, A6.15.4.4 states that elevator power shutdown is to have a delay so that the cab can be returned. While the elevator controller responds to the smoke sensor signal, and the door is opened, I don't think they have an auxiliary contact to tell me this. As the timing would change with the building height, elevator speed, and if primary or secondary floor, timing does not make sense. Has anyone figured this out?
 