Re: Elevator Air Cond. Circuit
My read on this is as follows: IF an A/C unit is installed, THEN it must be served by a dedicated branch circuit. I may be splitting a very fine hair here, but I believe the key to understanding 620-22(B) (1999 version) is to focus on the first sentence, and in particular upon the single occurrence of the word ?the.? The exact wording of this sentence is, ?A dedicated branch circuit shall supply THE (my emphasis) air-conditioning and heating units on each elevator car.? This does not require that an A/C unit be installed, nor that a dedicated branch circuit be provided, just in case the owner decides to install an A/C unit sometime in the future. If there is no A/C unit, then you don?t need to install a dedicated branch circuit for an A/C unit.
Good luck on this one. The Inspector might read the article differently, and can easily call it the other way.