Coachmike
- Morris County, NJ
- Electrical Contractor
Just as bad. The primary neutral on a wye-delta transformer should be left floating, as if it was a delta primary.Transformer neutral connection is bonded to ground.
Whats the nameplate amps of the drive?Two elevator cars running in a self storage facility. Car #1 is on it's 2nd transformer and has same issue as original transformer.
Transformer info below. According to the elevator co. they have replaced the VVVF drive- an AC Regeneration Unit.
Car#2 has no issues with similar equipment.
Now I see, the transformer is actually a wye autotransformer not a wye-wye isolation style. You do not have a separately derived system.Just as bad. The primary neutral on a wye-delta transformer should be left floating, as if it was a delta primary.
Wait, you have a wye-wye transformer, but the secondary neutral is floating? That sounds wrong by itself..
You're right. I didn't look at the image. A neutral is needed.Now I see, the transformer is actually a wye autotransformer not a wye-wye isolation style. You do not have a separately derived system.
Agreed. You do need a source neutral run to the transformer.By bonding the 'secondary' neutral to ground, you have effectively created a neutral to ground point different than the one at your 208V service. I believe you should run a neutral conductor from your source to the autotransformer and end it there, do not rebound it at the transformer. Bond the transformer core and enclosure to your EGC.
effortingStill need the nameplate info of the drive.
I would contact them to be sure, but I believe the neutral is required for the secondary voltages to be steady.Engineers drawings show 3 phases and a ground. No neutral.
For clarity, a neutral should be run from source panel to N.
Yes, grounding always. If #2 works wired the same, you need to find out what is different between them.And the transformer case should be grounded via EGC.
Both Car's transformers are wired the same and car #2 has no issues.
I know old thread, but Schindler is providing same transformer to us and it's blowing the primary fuses with no load attached. Any suggestions?Two elevator cars running in a self storage facility. Car #1 is on it's 2nd transformer and has same issue as original transformer.
I would think 100A primary (low voltage) side might even be too small given the spec says input FLA is 88.8A. But you need to select your fuse based on the time current information provided for the inrush current.low-peak, dual element time delay. This is from their submittals. Sent the transformer out with 20a fuses on the primary and 50a fuses on the secondary.
We have 60a ocp on primary 208v feeding Schindler transformer. Guessing that even the 50a primary fuse is too small.We had 60 amp OCP on primary 208v
and 40 amp OCP on secondary 480v
On our 20 KVA transformer feeding the Schindler MRL elevator.