We are encountering a problem more and more these days, and all of the solutions we know about are bad ideas. The issue is the short circuit current rating of elevator controllers, and several local jurisdictions are making an issue out of it. Most often it is shown as 5,000 amps, and occasionally is shown as 10,000 amps. The available fault current is often above 20,000 amps, and the elevator manufacturers are not willing to get their equipment tested and listed for higher fault currents. The solutions I have seen used include 1:1 transformers, increasing the length of the feeders, and installing current-limiting fuses. That last item is not viable, if the elevator controller has circuit breakers that serve the motor loads. A coworker just suggested feeding the elevators from a 208 volt bus, and using a 208-480V step up transformer to insert some impedance into the circuit.
Anyone have any better ideas?