hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
For high rise building, I have passenger elevator 30HP, FLA of 40A and freight elevator 40HP, FLA of 53A. Engineer used 430.52 to size the fused disconnect fuse and breaker in the panel.
So for freight elevator 40x1.75= 70A
and for passenger elevator 53x1.75=90A
I can see for fuse he used 175% but for breaker can one use 175%? I see 250% table 430.52
So for freight elevator 40x1.75= 70A
and for passenger elevator 53x1.75=90A
I can see for fuse he used 175% but for breaker can one use 175%? I see 250% table 430.52