Good day! I have some questions on an elevator I was asked to feed power to. Here are the specs I was given:
25 HP Elevator Motor
Motor nameplate rated current at rated horsepower - 69 amps
Motor locked rotor current for solid state starting - 207 amps
Single phase control load on main supply is 1.3 amps
Motor Code Letter B
They recommend a 100 amp fused disconnect.
My questions:
This facility has 1PH, 240V power. I am installing a phase convertor to get 3 PH power.
1 - From what I have been looking at, I need to protect for 89 amps (69 x 1.25 = 86.25 ---- Motor Code Letter B = 3.54% ----- 86.25 x 3.54% = 89.3 amps)
So, I would protect with a fused disconnect with 100A fuses. (Code recommends a little higher to eliminate nuisance tripping which might trap people in the elevator)
2 -I have to first protect the phase convertor - 100A ?
3 - After the phase convertor, motor controller protection - 100?
4 - They asked for a pit sump pump, GFCI, and lights which have not been roughed in. I can get the GFCI and lights from a circuit in the elevator equipment room. Might need more juice for the sump pump. To get that is there anything that
says I couldn't use a load center with main breaker for the first disconnecting means and feed the phase convertor and sump pump out of that?
25 HP Elevator Motor
Motor nameplate rated current at rated horsepower - 69 amps
Motor locked rotor current for solid state starting - 207 amps
Single phase control load on main supply is 1.3 amps
Motor Code Letter B
They recommend a 100 amp fused disconnect.
My questions:
This facility has 1PH, 240V power. I am installing a phase convertor to get 3 PH power.
1 - From what I have been looking at, I need to protect for 89 amps (69 x 1.25 = 86.25 ---- Motor Code Letter B = 3.54% ----- 86.25 x 3.54% = 89.3 amps)
So, I would protect with a fused disconnect with 100A fuses. (Code recommends a little higher to eliminate nuisance tripping which might trap people in the elevator)
2 -I have to first protect the phase convertor - 100A ?
3 - After the phase convertor, motor controller protection - 100?
4 - They asked for a pit sump pump, GFCI, and lights which have not been roughed in. I can get the GFCI and lights from a circuit in the elevator equipment room. Might need more juice for the sump pump. To get that is there anything that
says I couldn't use a load center with main breaker for the first disconnecting means and feed the phase convertor and sump pump out of that?