elevator feeder GFI protected

Status
Not open for further replies.
Re: elevator feeder GFI protected

No, when the code uses the term ground-fault protection, it doesn't necessarily mean ground fault protection for persons or equipment (GFCI, GFPE). Every overcurrent device does three things. It protects circuit conductors from overloads, short-circuits, and ground-faults.

In this case, ground-fault protection means a device is required to protect against ground-faults and short circuits but not necessarily overloads.

A GFCI device will limit ground faults to around 5mA. GFPE devices will limit ground-faults to around 30mA. A typical breaker can withstand a ground-fault to 10,000A.
 
Further clarification requested on old question

Further clarification requested on old question

bphgravity,
I understand that 620.61 is not intended to require personnel protection (GFCI, etc.). However, are you saying that 620.61 does NOT require the elevator feeder C.B. to include a GF trip mechanism at all? If so, I guess I don't see how the section can be intrepreted as such.
 
However, are you saying that 620.61 does NOT require the elevator feeder C.B. to include a GF trip mechanism at all?
This section is calling for nothing more than any standard OCPD. When the code wants additional protection it will use the term "ground-fault protection of equipment".
Don
 