Currently working on a large hospital in the Midwest. With the abundant amount of information in the NFPA 70, 101 and others, I am getting caught up with service to Elevators.
It's my understanding, according to NEC 517.32 that wiring of the Elevator cab lighting, control, communications and signal system are to be mechanically protected by ways of 517.30 (C)(2). I also understand that if I have elevators on the emergency system 517.34 (B) (2) they would need to comply with 517.30 (C)(2).
However - 517.30 (C)(2) never makes mention any fire protection rating of any kind. They mention MI cable, and I do not want to assume that this means that the feeder is fire rated.
My question is about the need (if any) for fire rating of the Elevator feeder from my distribution switchgear to the elevator control/machine room. When do I need to have fire rating for power feeds to an elevator? Or does the shaft rating and recall of the elevator cover in the event of a fire.
It's my understanding, according to NEC 517.32 that wiring of the Elevator cab lighting, control, communications and signal system are to be mechanically protected by ways of 517.30 (C)(2). I also understand that if I have elevators on the emergency system 517.34 (B) (2) they would need to comply with 517.30 (C)(2).
However - 517.30 (C)(2) never makes mention any fire protection rating of any kind. They mention MI cable, and I do not want to assume that this means that the feeder is fire rated.
My question is about the need (if any) for fire rating of the Elevator feeder from my distribution switchgear to the elevator control/machine room. When do I need to have fire rating for power feeds to an elevator? Or does the shaft rating and recall of the elevator cover in the event of a fire.