Electromatic
Senior Member
- Location
- Virginia
- Occupation
- Master Electrician
Dang elevator codes are driving me crazy! I'm in the final steps of a new install in an existing business-type building (restaurant 1st floor, office space 2nd, unfinished 3rd). There are sprinkler heads at the top of the shaft and in the pit, and there is a smoke detector at the top of the shaft. It is a machine room-less system with the gear sitting in a cowling in the shaft on the 1st floor.
There is an exhaust fan at the top of the shaft. All our plan says is to provide power. I would imagine that the fan would be controlled by the smoke detector at the top of the shaft. However, there are two trains of thought on its operation. Is it normally on then turns off if the detector is activated? This would help stop air flow to a fire. Or is it normally off and turns on when the detector is activated? This would vent smoke from the shaft during a fire.
All I can find in the IBC talks about machine room venting to maintain temperature for equipment. ASME 17.1 just says when required, hoistways shall be provided with means to prevent the accumulation of smoke and hot gases.
Also, if anyone wants to weigh-in on the pit wiring and devices needing to be NEMA 4 or even 3R, I'll listen. I read some other threads here and have gone through ASME 17.1. Again, there is a sprinkler in the pit. I'm of the opinion that the pit accessories (convenience receptacle, etc.) do not have to be any type of wet location rated. NEC doesn't say anything like that, and the ASME talks about elevator electrical equipment needing to be NEMA 4. I take that to refer to the actual elevator equipment, not the pit accessories, especially since I don't see how you would achieve a NEMA 4 receptacle.
Thanks for any thoughts and reading this pseudo rant!
There is an exhaust fan at the top of the shaft. All our plan says is to provide power. I would imagine that the fan would be controlled by the smoke detector at the top of the shaft. However, there are two trains of thought on its operation. Is it normally on then turns off if the detector is activated? This would help stop air flow to a fire. Or is it normally off and turns on when the detector is activated? This would vent smoke from the shaft during a fire.
All I can find in the IBC talks about machine room venting to maintain temperature for equipment. ASME 17.1 just says when required, hoistways shall be provided with means to prevent the accumulation of smoke and hot gases.
Also, if anyone wants to weigh-in on the pit wiring and devices needing to be NEMA 4 or even 3R, I'll listen. I read some other threads here and have gone through ASME 17.1. Again, there is a sprinkler in the pit. I'm of the opinion that the pit accessories (convenience receptacle, etc.) do not have to be any type of wet location rated. NEC doesn't say anything like that, and the ASME talks about elevator electrical equipment needing to be NEMA 4. I take that to refer to the actual elevator equipment, not the pit accessories, especially since I don't see how you would achieve a NEMA 4 receptacle.
Thanks for any thoughts and reading this pseudo rant!