designer82
- Boston
Working on a project where the building is single phase. Elevator vendor is providing a 3 phase elevator motor with a controller that has an integral single to 3 phase converter.
They show the specs for the 3 phase motor on the elevator drawings. These specs match NEC Table 430.250 for the 3HP motor they're providing (208V/3PH/60h, 10.6Amp)
Issue is they don't show the single phase input requirements for the controller.
I have requested this info but they don't respond and owner wants the stamped engineering drawings asap.
Would you put your foot down and say either provide that info or no drawings or would you just use NEC Table 430.248 to get the equivalent single phase ratings and apply it to the inverter input. In this case per table 430.248 (17 Amps at 230V/1/60)
thanks
thanks