I have a project where an elevator changed from a 25HP to 50HP (208/3), midway through the project. Inititally, we had a 125A CB for the elevator feed, and a 2" conduit for the feeder. The max size CB that the electrician can get for the MDP without holding up the project is a 200A CB. How concerned would you be that this circuit breaker is going to trip?
50HP @ 208/3 is 143 FLA per NEC table 430, but according to the elevator shops, the FLA is 156 which likely takes into account the motor + controls etc...
The application is a furniture store and the elevator will likely be used fairly infrequently but I am concerned about the initial startup and filling the store.
I know this is kind of a loaded question.
50HP @ 208/3 is 143 FLA per NEC table 430, but according to the elevator shops, the FLA is 156 which likely takes into account the motor + controls etc...
The application is a furniture store and the elevator will likely be used fairly infrequently but I am concerned about the initial startup and filling the store.
I know this is kind of a loaded question.