Elevator on Generator, Emergency vs Legally Required?

Status
Not open for further replies.

Shujinko

Senior Member
I have a project which is using the elevator as a path of egress, but not a high-rise. Does this egress elevator have to be on the Emergency System (NEC Art 700) or Legally Required System (NEC Art 701)?
 
I would put an elevator that is part of the required means of egress on the emergency branch. If it is not part of the required means of egress, but is an owner preference to have an elevator on generator power I would put that on the optional standby branch.

I make the following distinction between articles 700 and 701 in my mind. If it is required to help people get out of the building, it is on the emergency branch. If it helps the fire fighters do their jobs or controls smoke, it is on the legally required branch.
 