I have not yet done a residential elevator. I hear they are more common. Keep us posted on how it goes!Paul B said:A little off topic but do many of you guys come across elevators in residential? Getting ready to quote on a job with one.
Maybe 1 every 2 or 3 years. Resi elevators don't normally have a pit. The pump or motor sits on the floor of a closet near the elevator, or in the attic. There isn't much to a resi elevator. The last one I did just plugged in. I should say that I don't install them... the elevator people did that. I just put the receptacle there for them.Paul B said:A little off topic but do many of you guys come across elevators in residential? Getting ready to quote on a job with one.
I'm pretty sure it was a 240V dryer rec, so I'm not rightly sure.ItsHot said:Just a receptacle? I might be able to handle that! Ground up, or ground down?
JohnJ0906 said:The last elevator I did (residential) I provided a 240v 30 amp circuit to a disconect, and the elevator guys took care of the rest.
I did wire the equipment room with light and GFCI receptacle, and provide a telephone line.
TwinCitySparky said:I dont know how an elevator could be installed without a pit... Unless you dont mind stepping up into it at the basement level. (Kinda defeats the purpose)![]()
Two posts that lift a plate up and down.TwinCitySparky said:I dont know how an elevator could be installed without a pit... Unless you dont mind stepping up into it at the basement level. (Kinda defeats the purpose)![]()
TwinCitySparky said:Yup - Almost the same requirements for my last install except the elevator guys asked me to install a 3 phase 30A disco so they could run one one extra conductor (battery power?) thru the disco for their hydraulics - They also required a second disconnect in the equip. room for the elevator lighting. The equipment room and the pit (yes this resi install has a pit) needed GFI power. The pit required a protected light with switch.
I dont know how an elevator could be installed without a pit... Unless you dont mind stepping up into it at the basement level. (Kinda defeats the purpose)![]()
Well, yeah. Even the one I talked about that had two posts that lifted up and down a plate had a little indent in the floor maybe 3" deep for some understructure of the plate to go down into.JohnJ0906 said:I see them with depressions not pits -
Were getting ready to do the install of conduit/service to the elevator.Mlummiss said:Is EMT allowed in elevator pit
Paul B said:A little off topic but do many of you guys come across elevators in residential? Getting ready to quote on a job with one.
mdshunk said:Two posts that lift a plate up and down.
usually all the electrician does with elevators is supply power and the elevator company does the rest.Paul B said:A little off topic but do many of you guys come across elevators in residential? Getting ready to quote on a job with one.