1996 ASME A17.1 Rule 102.2:
(c) Standard sprinkler protection conforming to the requirements of ANSI/
NFPA 13 shall be permitted to be installed in these spaces, subject to the
following.
(1) All risers and returns shall be located outside these spaces.
(2) Branch lines in the hoistway shall supply sprinklers at not more than
one floor level.
(3) Means shall be provided to automatically disconnect the main line
power supply to the affected elevator upon or prior to the application of
water from sprinklers located in the machine room or in the hoistway more
than 2 ft (610 mm) above the pit floor. This means shall be independent of
the elevator control and shall not be self-resetting. The activation of sprinklers
outside of the hoistway or machine room shall not disconnect the
main line power supply.
(4) Smoke detectors shall not be used to activate sprinklers in these spaces
or to disconnect the main line power supply.
(5) When sprinklers are installed in the hoistway, all electrical equipment,
except earthquake protective devices conforming to the requirements of
Rule 2409.1b(4), located less than 4 ft above the pit floor shall be:
(a) weatherproof (NEMA4); and
(b) wiring shall be identified for use in wet locations in accordance with
the requirements in ANSI/NFPA 70.