Could some one give me a rundown on how a conventional system is wired for elevator recall... (not addressable)
I talk to people about this all the time. If you follow the letter of the Fire Alarm Code, I don't know how to do it properly with most conventional systems.
...The most important hurdle is the code requirement for the relays to be within 3 feet of the device or circuit it is controlling. This normally means the relays need to be mounted in the elevator machine room and is best done with addressable relays. If your conventional panel has a relay card that can be remote mounted and supervised then maybe you can use a conventional panel...
I have 4 wire smoke detectors with a relay, it should be simple that way when the smoke goes into alarm it will trip the function required depending on where its located. primary or alternate recall.
Would i need to have a separate zone for the elevator recall?
How would i trip the shunt assuming i have a 4 wire heat detector in the machine room?
couldnt you use a smoke detector with a built in relay base such as the system sensor B116LP, then go to a relay mounted in the elevator machine room or where ever the elevator controls are located which would then be wired to the primary recall/secondary recall/firehat/shunt inputs of the elevator controls? bring AUX power to the detectors wired in as N/O with the relays so that an activation would close the contacts thus sending power down to the relays mounted near the elevator equipment that would then drive the fire functions of the elevators?