Guys,
I just failed an elevator inspection because inspector state I can not have a junction box gutter style NEMA 1 under elevator disconnect. Is this correct? Crew installed this because was easy to land conduits coming out of slab. He cited 314.7 (a) (3) could not find anything. Also he make us cut and fill with concrete stub ups from MPOE for phone line.
Please any comments would be great.
I just failed an elevator inspection because inspector state I can not have a junction box gutter style NEMA 1 under elevator disconnect. Is this correct? Crew installed this because was easy to land conduits coming out of slab. He cited 314.7 (a) (3) could not find anything. Also he make us cut and fill with concrete stub ups from MPOE for phone line.