LOOKING FOR A RESOLUTION TO ELEVATORS SHUNTING DURING A GENERATOR RUN AND POWER CUT OVER.
BACK STORY.
ORIGINALLY THE SHUNTS TRIP HAD NOTIFIER FCM FOR SHUNTING AND RECALL.
WE FOUND THAT 24V WAS GETTING THROUGH THE FCM WHEN EMERGENCY POWER IS SWITCHING OVER. WHICH CAUSED THE SECONDARY RELAY TO CHANGE STATE CAUSING SHUNT AND RECALL.
PER NOTIFIER I CHANGED FCM TO FRM RELAYS.
APPEARED TO WORK. TESTED 1 BANK OF ELEVATORS FUNCTIONED PROPERLY.
I COMPLETED REPLACING ALL FCMS FOR FRMS FOR ALL ELEVATORS.
ONCE COMPLETED THE ENGINEERS TESTED THE GENERATORS AND ALL ELEVATORS SHUNTED DURING POWER CUT OVER.
SO CANT SEEM TO FIND THE PROPER CASUE OF THIS ISSUE. EITHER 24V IS GETTING THROUGH THE FRM RELAY OR THE ISSUE IS THE ACTUAL SHUNT TRIP BREAKER.
ANY IDEAS OR INFORMATION WORLD BE APPRECIATED.
HAS ANYONE ELSE DEALT WITH THIS BEFORE?