Elevator sump pump receptacle

Status
Not open for further replies.
Not sure how 2020 addressed it but 2017 seems a bit ambiguous.
620.24 requires a duplex receptacle and reference 620.85 where GFCI is required except on single receptacles for sum pump.
Seems you would need a duplex GFCI & allowed a simplex non-GFCI.
 
Not sure how 2020 addressed it but 2017 seems a bit ambiguous.
620.24 requires a duplex receptacle and reference 620.85 where GFCI is required except on single receptacles for sum pump.
Seems you would need a duplex GFCI & allowed a simplex non-GFCI.

Engineer provided sump pump elevator with GFCI. I am not sure 2017 section 630.85 says shall be permitted does that also mean to say that simplex receptacle should not be gfci at all?
 
Engineer provided sump pump elevator with GFCI. I am not sure 2017 section 630.85 says shall be permitted does that also mean to say that simplex receptacle should not be gfci at all?
The 2017 rule does not require a singe receptacle for a sump pump to have GFCI protection. There is nothing that would prohibit that receptacle from having GFCI protection, and a change in the 2020 code requires that single receptacle to have GFCI protection.
 