dannay Member Location West Simsbury, CT Apr 2, 2004 #1 Does the receptacle located at the sump pit (GFI protected ofcourse) have to be on a seperate C/B and branch circuit from a convenience outlet in the elevator machine room?
Does the receptacle located at the sump pit (GFI protected ofcourse) have to be on a seperate C/B and branch circuit from a convenience outlet in the elevator machine room?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 2, 2004 #2 Re: ELEVATOR SUMP PUMP Yes. See 620.23(A). Don
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 2, 2004 #3 Re: ELEVATOR SUMP PUMP The sump pump receptacle (single) does not have to be GFCI protected, see 620.85 Also read 620.24 Roger
Re: ELEVATOR SUMP PUMP The sump pump receptacle (single) does not have to be GFCI protected, see 620.85 Also read 620.24 Roger