- Location
- New Jersey
- Occupation
- Journeyman Electrician
How would you determine the minimum conductor size for this VFD for an elevator motor? Seems simple to me 85 amps. Is there a different formula for elevator drives?
input current * 125%
67.31 amps * 125% = 84 amps
Someone is saying otherwise.
Of the VFD.Aren't we only concerned.with the input amps?
Of the VFD.
Yes, the question is for sizing the conductors based on the input current to the drive, do you use the 67.31 amps or do you need to factor in the 125% as required by 430.22(A)?
620.13 brings us to 430.22E. This tells us we need the rating of the motor.
Well that made my eyes cross and wonder WTH.
430.122(A) sounds better. Input current of the drive is my answer and that would be based on the 67.31 amps. Not the output of 75.
620.13(B) Conductors Supplying a Single Motor Controller.
Conductors supplying a single motor controller shall have an
ampacity not less than the motor controller nameplate current
rating, plus all other connected loads. Motor controller nameplate
current ratings shall be permitted to be derived based on
the rms value of the motor current using an intermittent duty
cycle and other control system loads, if present.
I don't believe an elevator is continuous duty so wouldn't 620.13
That's the question, does that override 430.122(A) which requires the drive conductors to be sized at 125%.
But 620 does not and Chapter 6 overrides chapters 1-4
I don't believe an elevator is continuous duty so wouldn't 620.13
Does it matter if the elevator is continuous duty, or is the relevant question is the motor rated as continuous duty?
Let me state I am not an expert on elevators but going from what I see and what I know about the NEC is that the conductors for the VFD in an elevator would be based on art. 620 which overrides any other articles.
The only info I see in 620 that mentions continuous is that an escalator motor must be rated continuous duty. An elevator motor is not continuous but it still can be rated continuous duty- I don't think that is the same
The way I 'm reading it 620.13(B) is for the motor controller (VFD) so as Dennis has pointed out that would be the applicable section for the conductors feeding the drive. The conductors between the drive and the motor are not relevant in determining the size of the conductors to the elevator controller.