I assume that it is really on the discretion of the State's code and the AHJ. "Legally required" for both emergency and standby is exactly that.
 
The NEC only tells you how to wire something once some other code has told you what type of system supplies the elevator.
 
Can folks point me to the right code? Or is it purely AHJ discretion?
Do you know if your area uses IBC, or International Building Code?
Is the building considered a high rise?

It looks like it depends on how many stories, and if elevator is used for egress means.
If required, it looks like elevator machine room ventilation/AC will also be required to be powered as well, along with other requirements that, some probably would not be your responsibility, but elevator contractor instead. Design requirements.

So it may begin with building code, and NFPA, and then NEC.
I found a couple things online that hopefully will give you some kind of reference point to check. But not enough detail.


This link Is dated 2005, but discusses the IBC , and gives reference numbers to go by, if the article/ chapter numbers are still correct.

 
Do you know if your area uses IBC, or International Building Code?
Is the building considered a high rise?

It looks like it depends on how many stories, and if elevator is used for egress means.
If required, it looks like elevator machine room ventilation/AC will also be required to be powered as well, along with other requirements that, some probably would not be your responsibility, but elevator contractor instead. Design requirements.

So it may begin with building code, and NFPA, and then NEC.
I found a couple things online that hopefully will give you some kind of reference point to check. But not enough detail.


This link Is dated 2005, but discusses the IBC , and gives reference numbers to go by, if the article/ chapter numbers are still correct.


Yes, it does use the IBC.

8 stories?

The thing is I've seen buildings go both ways, with or without back on the elevators.
 