From Table 430.250 20 hp 3phase 208 volts we get 59.4 amps but I would use nameplate.sparky76 said:Hey guys. Don't have my book in front of me. I'm looking at a 20HP/208V/3phase (duh) motor. What size breaker am I going to need? Thanks in advance.
Wouldn't an elevator motor be considered high torque? I don't know just asking.haskindm said:430.6(A)(1) tells you to use the table values INSTEAD of the namplate rating to determine the size of the short-cicuit and ground-fault protection (circuit breaker). The nameplate rating would ONLY be used to size the overload protection (heater).
iwire said:The elevator companies have always told us the feeder size, usually much larger then really needed then they fuse it down at the disconnect we provide.
peter d said:Any idea why they do this?
I'm guessing it's so they're covered in case they decide to put a bigger motor in?
iwire said:I do know they get stuck in their ways, I did an elevator retrofit and the elevator guy explained to me his equipment had to have a copper EGC or it would not operate, if I tried to use the conduit as ground he would know. He also explained how it is a code violation to use the conduit as ground. :roll:
peter d said:I'm sure you thanked him afterward for enlightening an ignorant electrician like yourself.
That wasn't the Foxboro elevator, was it?
iwire said:I believe they asked for a 480V 3PH 100 amp feeder and then installed 65 amp fuses at the disconnect.
iwire said:He got his ground and I did not bother getting into it with him.
chris kennedy said:Tuesday Jan. 29th 2008. 5:29PM
Bob admits he run a Cu. EGC in EMT.
I'll go ahead and save this one.:grin: