we are sizing a circuit breaker for an elevator 20hp motor 208volt 3-phase, full load amp
my square 'd' slider and the code sayes 62.1amps time 1.25 equals 77.6, i put a 100 amp
breaker.
now when we get the spec from the elevator they say the name plate full load amps equals
95amp, i will need a 150 c/b. any help
thanks
my square 'd' slider and the code sayes 62.1amps time 1.25 equals 77.6, i put a 100 amp
breaker.
now when we get the spec from the elevator they say the name plate full load amps equals
95amp, i will need a 150 c/b. any help
thanks