460V 25 HP elevator. Single elevator. Shop drawings state NEC intermittent 30 & 60 minute rated factors can be applied. Motor nameplate rated current is 36.0 amps. Per shops switch should be 3-pole 60A with 60A dual element fuses. NEC 2008 applies.
Branch circuit conductors are sized per 620.13(A), which refers you to 430.22(A) and (E). As manufacturer states intermittent factors can be applied then 430.22(E) is the correct paragraph. The table states 90% of nameplate rating applies. 36.0 * 0.9 = 32.4A.
Per Table 310.16 you can conservatively use the 60C column which allows #8 CU, or could assume all lugs are rated 75C which allows #10 CU.
I specified #8s with a 60A fused disconnect and 60A class J fuses. This meets code and manufacturer requirements, yes?
Branch circuit conductors are sized per 620.13(A), which refers you to 430.22(A) and (E). As manufacturer states intermittent factors can be applied then 430.22(E) is the correct paragraph. The table states 90% of nameplate rating applies. 36.0 * 0.9 = 32.4A.
Per Table 310.16 you can conservatively use the 60C column which allows #8 CU, or could assume all lugs are rated 75C which allows #10 CU.
I specified #8s with a 60A fused disconnect and 60A class J fuses. This meets code and manufacturer requirements, yes?