Having done nine elevators in the last two years, I ensure that we get the following circuits from the panel to the elevator machine room. From that machine room, I can get any circuit to it's location.
1. Pit lighting/GFI
2. Sump pump-elevator pit
3. Machine room lighting/GFI
4. Shunt trip
5. Exhaust fan-some type of ventilation will be required in the machine
room
6. Cab light circuit
7. Spare-I always pull a spare to that room.
Keep in mind that there are minimum lighting requirements in the elevator machine room, elevator pit, and the elevator lobby. Here in Ohio, I ensure that I have 10-foot candles at each location. The state elevator inspector here takes a measurement at each location and in the lobby, this measurement is taken with the doors closed.
Fire alarm drawings should clearly show what is required, I make provisions to include four relay modules in the elevator machine room.
1. Primary recall
2. Secondary recall
3. Fireman's hat
4. Shunt trip
I use a four square box for each device, locating them close to the elevator machine. Keep in mind that primary recall, secondary recall, and hat will terminate in the elevator machine. I am required to have one smoke detector and at least one heat detector, located within 24" of a sprinkler head. If more than one sprinkler head, a heat detector is required within 24" of each location.
The elevator machine will require a phone line, as well.
Hope I have been of some help. Befriend the elevator mechs, they won't steer you wrong. If you like, I could post some pics of the elevators we are currently building.