mshields
Senior Member
- Location
- Boston, MA
To my knowledge patient rooms be they in I1 or I2 facilities must have smoke detectors. Is any one aware of an exception to this rule? I've got a hospital client who would like to be rid of them.
Yes - I did look and in MA there is an amendment for I1 facilities requiring smoke detectors in sleeping area's but there is no such amendment for I2 and the actual IBC verbiage seems to imply that smoke detector would only be required in the room if one wanted to forego smoke detection in the corridors.
So I think they are not required actually.
To my knowledge patient rooms be they in I1 or I2 facilities must have smoke detectors. Is any one aware of an exception to this rule? I've got a hospital client who would like to be rid of them.
You are correct, under the IBC only corridors and spaces open to the corridor must be detected. There is an exception to detect the patient rooms with a visible signal at the door in lieu of corridor detection.
That seems to imply if the detectors are eliminated in the patient rooms, the patient rooms would have to have automatic closers on the doors.