mstrlucky74
Senior Member
- Location
- NJ
Know we spoke about this before. Have 3 separate vertical riser shafts in an electrical closet as shown. I’m running EM conduits. I’m running EMT and XHHW. According to 700.9 I think I’m okay and maintaining a hour rating as the closet is 1 hour rated and I fulfill 700.9 D4. The only thing that’s a little fuzzy is that D4 says “only emergency circuits”. Would it matter of there was a normal conduit riser in same closet right next to the EM? Thanks.