EM Circuits

If they are truly EM circuits yes. Take some time and read article 700.
 
Granted I only read 700 and 701 for 20 minutes they are( as I thought) hard to distinguish the difference. Meaning if I'm looking at a job with emergency power riser what in the design would indicate it's EM or legally required standby?
 
Granted I only read 700 and 701 for 20 minutes they are( as I thought) hard to distinguish the difference. Meaning if I'm looking at a job with emergency power riser what in the design would indicate it's EM or legally required standby?
The NEC does not tell you which is which, the NEC only tells you how to wire them after some other code or standard has told you which is which.
 
The NEC does not tell you which is which, the NEC only tells you how to wire them after some other code or standard has told you which is which.9k.. ut
Ok. But I'm trying to determine ...on a job we have...if the em lighting needs to be separate raceway. 700 it does and 701 it doesn't . I can't determine which article my em lighting falls under
 
Ok. But I'm trying to determine ...on a job we have...if the em lighting needs to be separate raceway. 700 it does and 701 it doesn't . I can't determine which article my em lighting falls under
If I’m not mistaken a lot your projects happen in NYC. If that’s true then it should be pretty easy as NYC local amendments states something like all 701 loads are to be treated like article 700.
 
Ok. But I'm trying to determine ...on a job we have...if the em lighting needs to be separate raceway. 700 it does and 701 it doesn't . I can't determine which article my em lighting falls under
Are the emergency lights powered by a generator? Are there battery powered emergency lights. How many transfer switches are there?
 