mjc1060

Senior Member
These pictures are part of my earlier post on open wiring. I have been told that there is not a problem with open wiring. These pictures are of a battery light. To me, the real emergency is the fact that the armored cable is not bonded to the J-box. If you look closely, you will see that there is no J-box.

The fixture is plastic. If there is a fault, where would the 120v potential go?

Comments appreciated. Thanks!
 

Attachments

  • photo1.JPG
    photo1.JPG
    28.7 KB · Views: 1
  • photo2.JPG
    photo2.JPG
    29 KB · Views: 1
  • photo3.JPG
    photo3.JPG
    26.2 KB · Views: 1
300.15 requires a box where conductors are spliced or terminated so open wiring is not permitted. Also in the pictures the AC cable is not properly connected to the fixture with a proper connector. The sheath of AC cable is the EGC so with a plastic enclosure there is no way to ground the fixture if the fixture is equipped with a wire or EGC terminal.

Chris
 
These pictures are part of my earlier post on open wiring. I have been told that there is not a problem with open wiring. These pictures are of a battery light. To me, the real emergency is the fact that the armored cable is not bonded to the J-box. If you look closely, you will see that there is no J-box.

The fixture is plastic. If there is a fault, where would the 120v potential go?

Comments appreciated. Thanks!

Who told you this? A painter?
 