Have a job that's budgetary with a bunch of recessed 2x2's and 2x4's. How would quantify how many lights would have to be emergency lights? Thanks.
Have a job that's budgetary with a bunch of recessed 2x2's and 2x4's. How would quantify how many lights would have to be emergency lights? Thanks.
Have a job that's budgetary with a bunch of recessed 2x2's and 2x4's. How would quantify how many lights would have to be emergency lights? Thanks.
Ballasted lighting with battery backup, right? Most manufacturer's will give you a diagram or graph that gives the cone of minimum illumination for the fixture at a given height. Space the backup units to give you the required illumination along the path of egress (1 foot-candle/11 lux at the walking surface, 1008.2.1, IBC 2015).
An engineer will need to do that calc, not the estimator or contractor. So be careful.
It depends on the jurisdiction as to who signs and seals what. From a technical perspective, any lighting supplier should be able to take a reflected ceiling plan and work it out for their customer. There isn't much magic sauce for an engineer to apply.
It all depends on the project in my opinion and when dealing with emergency egress lighting as a life safety issue; it can come back to bite you if done with just placing them where one thinks they should go.There isn't much magic sauce for an engineer to apply
That is for normal power. Emergency power only requires an average of 1 footcandle per 1008.3.5 with max/min ratios of 40:1. In my experience, this requires photometric calculations unelss you've used the same fixture in the same scenario (ie corridor of same width, etc). For example, using an emergency egress light that says it can be spaced every 20ft for corridors of width of 5ft may not also be able to work in large auditoriums, etc.Space the backup units to give you the required illumination along the path of egress (1 foot-candle/11 lux at the walking surface, 1008.2.1, IBC 2015).
Have a job that's budgetary with a bunch of recessed 2x2's and 2x4's. How would quantify how many lights would have to be emergency lights? Thanks.
It all depends on the project in my opinion and when dealing with emergency egress lighting as a life safety issue; it can come back to bite you if done with just placing them where one thinks they should go.
That is for normal power. Emergency power only requires an average of 1 footcandle per 1008.3.5 with max/min ratios of 40:1. In my experience, this requires photometric calculations unelss you've used the same fixture in the same scenario (ie corridor of same width, etc). For example, using an emergency egress light that says it can be spaced every 20ft for corridors of width of 5ft may not also be able to work in large auditoriums, etc.
Good point Gadfly...definitely not worth wasting the time to send it out for a full design at this point. I overlooked his original goal and got too deep in the weeds..![]()