Re: EM lights vs. Egress lights
Tom thanks for the PM.
I will be using the 2000 IBC (International Building Code) for this, since I don't have the 2003 here at home. Be mindfult taht nothing relevent changed between the two, however.
Means of egress illumination is found in section 1003.2.11, and it states
The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied.
There are a couple of exceptions that aren't worth getting into.
Section 1003.2.11.1 goes on to say that such illumination shall be 1 foot candle measured at the floor level.
What this is saying is that anytime anybody is in the building, there must be lights that provide a minimum amount of illumination. This is just your typical lighting...not emergancy. The intent here is designing enough light, so that under non-emrgancy conditions a person can egress from a building easily.
Section 1003.2.11.2 goes on to state that such illumination needs to be supplied from an emergancy source (article 700, not 701) in a few different areas. These areas are basically limitted to the areas that, due to occupacny type and occupant load, require two exits.
Summary: All areas need 1 foot candle of light. Areas that require two exits need emergancy illumination.
Does that make sense?