EM vs LRSS

Status
Not open for further replies.

kjplmisano

New member
Mr Holt

I am in the process of renovating a college dorm.

Nearly all the existing branch conduit is poured in the slab.

Somewhere over the years a 30 kw generator, automatic transfer switch and 2 panels were added .

The branch circuits feeding the exit light and night light circuits were pulled in the same conduit as the normal power circuits.

There are no battery back up EM lights so the night light serves as the emergency lighting.

My question to you, is this system considered a Emergency System or a Legally Required Stand By System?

Other than as required by Art 517, how can you tell where an EM system is required or a LRSS?

Thanks

Ken Palmisano

Syracuse Merit Electric
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: EM vs LRSS

Ken, this would be up to the applicable AHJ be it state, local, institution, etc... for classification.

See 700.1 and 701.2

Roger
 