I have a geared motor for belt conveyor and its specs 1.5KW, 460V Y connected, 3.7rated current, 60hz and rated speed 1730rpm and module setting curret of 3.7A. Now i have just replaced it the same geared motor but big size which rated 2.2KW, 460V Y connected, 4.25rated current, 60hz and rated speed is 1705rpm.
Regarding 115% protection(4.25 x 1.15). With regards ,I set EMC to 4.25A module setting curret, expecting to trip fast before it reach 115% operation for protection of motor.
I have two option to check with actual current 4.25x1.5=4.375A and 4.25x2=8.5A whether the 4.25A module setting current is correct with the time frame to trip motor , the trouble with me is to determine the what is the tripping time (s) of 4.25 in EMC
Thanks for any comment and suggestion
Regarding 115% protection(4.25 x 1.15). With regards ,I set EMC to 4.25A module setting curret, expecting to trip fast before it reach 115% operation for protection of motor.
I have two option to check with actual current 4.25x1.5=4.375A and 4.25x2=8.5A whether the 4.25A module setting current is correct with the time frame to trip motor , the trouble with me is to determine the what is the tripping time (s) of 4.25 in EMC