The 2008 in section 250.20 D tells us if supplied with transfer equipment that switches the grounded conductor then it shall be grounded in accordance with 250.30A, it is by definition a separately derived system. The fine print note tells us that if a solidly interconnected grounded conductor, a 3 pole transfer switch, then the generator is not a separately derived system. I do not believe that you can have it both ways, a separately derived and not a separatelt derived system. From my understanding you cannot mix transfer switches, meaning thay all have to switch the grounded conductor or not switch it, the transfer switches cannot do both.
Fred