Designer69
Senior Member
My main question is on the E/G circuit breaker size(s) for the attached riser diagram. I am not sure if I should make them the same size as the breakers feeding the normal side of the ATS.
The C-2 and C-3 cables are sized for the connected loads (x 1.25%) of the downstream panels.
Also, an ovarall sanity check on the riser is appreciated. The emergency branch only has 1KVA worth of emergency lights but still required since emergency lights need emergency branch/ATS.
better pic here: https://ibb.co/iuHMoT
Thank You
The C-2 and C-3 cables are sized for the connected loads (x 1.25%) of the downstream panels.
Also, an ovarall sanity check on the riser is appreciated. The emergency branch only has 1KVA worth of emergency lights but still required since emergency lights need emergency branch/ATS.
better pic here: https://ibb.co/iuHMoT
Thank You