emergemcy light in battery room

Status
Not open for further replies.
Re: emergemcy light in battery room

Depending on the building, you could look in two places. If it is a public building, office warehouse, etc., your local building code may be the choice. If it is a battery room in a generating plant, switching station, etc., the NESC has requirements for buildings like that which are not subject to the local building codes.
Jim T
 
Re: emergemcy light in battery room

What do you mean by battery room? If the batteries supply power to some sort of life safety function there is a requirement. This is referenced by the FPN in NEC 517.32 to refer to NFPA 101 5.8 5.9
If we are talking about a storage room or a battery charging room, then no.
 