Emergency and Legally Required power system

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Existing high-rise building with emergency generator and (2) ATSs serving Emergency and Legally Required power system load.
In several floors, I saw they had electrical outlets inside IT rooms powered from panels belong to Emergency power system.

I think those outlets should be powered from Legally Required power system panels per NEC-700, correct? Thank you!
 
I guess it depends on what the equipment in the IT room does, but usually IT rooms would be optional standby article 702.

But I have never worked on a highrise project.
 