Could you help me with understanding the separation of Emergency and Normal power. I seem to be getting conflicting information on this topic. For example we have a job where we are changing out the main switchboard at a college. In order to get this done they're going to put on an electrical room as an addition.
The proposed drawings show the following equipment for this electric room addition as the following:
4000 AMP Switchboard 480/277 V, a Generator Switchboard, Emergency Panel and ATS, Optional Standby Panel and ATS, Legally Required Panel and ATS, and two normal 480/277 volt panels, and one normal 208/120 volt two tub panel and transformer.
I was always under the impression that you couldn't have normal and emergency power share the same room.
Doesn't NFPA 110 7.2.3 prohibit this?
NFPA 110 [FONT=arial, sans-serif]7.2.3 which states "Level 1 EPSS equipment shall not be installed in the same room with the normal service equipment, where the service equipment is rated over 150 volts to ground and equal to or greater than 1000 amperes"[/FONT]
The proposed drawings show the following equipment for this electric room addition as the following:
4000 AMP Switchboard 480/277 V, a Generator Switchboard, Emergency Panel and ATS, Optional Standby Panel and ATS, Legally Required Panel and ATS, and two normal 480/277 volt panels, and one normal 208/120 volt two tub panel and transformer.
I was always under the impression that you couldn't have normal and emergency power share the same room.
Doesn't NFPA 110 7.2.3 prohibit this?
NFPA 110 [FONT=arial, sans-serif]7.2.3 which states "Level 1 EPSS equipment shall not be installed in the same room with the normal service equipment, where the service equipment is rated over 150 volts to ground and equal to or greater than 1000 amperes"[/FONT]