Are heat detectors or Fire Alarm and Detection System (FADS) required to be tied-in for emergency boiler shutdown? Or, what are the requirements for emergency boiler shutdown for large industrial boilers?
 

eric9822

Senior Member
Location
Camarillo, CA
Occupation
Electrical and Instrumentation Tech
I believe you need to take a look at NFPA 85. It spells out the requirements for boiler and combustion safety shutdown systems.
 

muskiedog

Senior Member
Location
Minnesota
We have just installed two new boilers and were required to install emergency shut downs outside of the room at each entrance for emergency personnel.

This is code in minnesota

Minnesota Rules, Chapter 4715.

Subp. 3. Section 1006.9. IMC Section 1006 is amended by
adding a section to read as follows:

1006.9 Boiler shutdown switch. A manually operated remote
shutdown switch shall be located at the boiler room door and
marked for easy identification. The emergency shutdown switch
shall disable all power to the burner controls.

Exception: A single hot water boiler with a rated
input of less than 400,000 Btu/hr (117 kW).
 