emergency circuits in health care facilities

Status
Not open for further replies.
Do emergency 120v circuit in health care facilities need to be run in conduit or is hospital grade mc good enough?

(3) Mechanical Protection of the Emergency System. The wiring of the emergency system in hospitals shall be mechanically protected. Where installed as branch circuits in patient care areas, the installation shall comply with the requirements of 517.13(A) and (B). The following wiring methods shall be permitted:

I would say for the most part to achieve mechanical protection non- flexible metal raceways will be required.

assuming your health care facility is a hospital
 
Status
Not open for further replies.
Top