The 2020 NEC introduced the emergency disconnect for a 1 or 2 family household in section 230.85. The NYC amendments added an exception to that section, stating the following:
Section 230.85 – Add an Exception at the end of Section 230.85 to read as follows:
Exception: If the emergency disconnecting means cannot be located in a readily accessible outdoor location, or if the utility metering equipment is located indoors, 1 of the following disconnecting means shall be permitted:
1. A remote disconnecting means provided by the utility
2. An indoor shunt-trip disconnecting means with the control device located in a readily accessible outdoor location and marked, “Remote Emergency Disconnect”
3. An approved equivalent means
My question is regarding #2, with the shunt-trip. How do you power the control device located outside, that controls the indoor shunt-trip breaker? Do I bring 120 volts to the control device by tapping off one of the hot wires of the service entrance conductors? It would seem strange to bring 120 volts from a panel inside the house, since that panel would be on the load side of the shunt trip emergency disconnect and service equipment.
Section 230.85 – Add an Exception at the end of Section 230.85 to read as follows:
Exception: If the emergency disconnecting means cannot be located in a readily accessible outdoor location, or if the utility metering equipment is located indoors, 1 of the following disconnecting means shall be permitted:
1. A remote disconnecting means provided by the utility
2. An indoor shunt-trip disconnecting means with the control device located in a readily accessible outdoor location and marked, “Remote Emergency Disconnect”
3. An approved equivalent means
My question is regarding #2, with the shunt-trip. How do you power the control device located outside, that controls the indoor shunt-trip breaker? Do I bring 120 volts to the control device by tapping off one of the hot wires of the service entrance conductors? It would seem strange to bring 120 volts from a panel inside the house, since that panel would be on the load side of the shunt trip emergency disconnect and service equipment.